Following up on this topic, I have a similar question:
I'm installing several 120v, 20-amp branch circuits. The conductors are run from the panel to a pull box in one 2" conduit, and then spliced to serve individual loads branching out from the PB in seperate conduits. Because of the number of conductors in the 2" conduit, the wire was resized to #8, but is still spliced to #12 in the PB going out to the individual loads.
Question:
In reference to 250.122(B), would the EGC still need to be upgraded to #8 in the 2" conduit going to the PB even though it is spliced to #12 in the PB?
I'm installing several 120v, 20-amp branch circuits. The conductors are run from the panel to a pull box in one 2" conduit, and then spliced to serve individual loads branching out from the PB in seperate conduits. Because of the number of conductors in the 2" conduit, the wire was resized to #8, but is still spliced to #12 in the PB going out to the individual loads.