I came upon a job recently where the electrician needed to install a 200 Amp 3 phase subpanel.So he grabbed 100 Amps from each of 2 seperate 3 phase panels which are side by side,but on 2 differant meters. Is this outragous or what?Maybe it is typical workmanlike behavior.But it seems to actually be another friday afternoon job.:-?
 
its perfectly fine! code allows you to parallel feeders. you guys are just a bunch of hacks trying to take advantage of the customer by selling them a bigger service.

(is whats going through the head of the guy who did this)


i would have loved to seen that go boom if he got a phase swapped
 
This is highly dangerous for multiple reasons, one how do you go about shutting down the 200 amp panel ? second how do you keep the first panel from back feeding into the second panel and causing a potential hazard ?
 
Jesse,

This needs to be brought to the attention of the Electrical Inspector, or POCO , asap. This

booby trap could kill the 'meter person " who may need to work on the meter. If you are

not willing to get involved, make a call without giving your name. YOU MUST DO SOMETHING.

Jesse, make sure you are right, then do the right thing.
 
I came upon a job recently where the electrician needed to install a 200 Amp 3 phase subpanel.So he grabbed 100 Amps from each of 2 seperate 3 phase panels which are side by side,but on 2 differant meters.
How does he make sure the current is evenly divided? :confused: :)wink:)


Some peoples' children! :rolleyes:
 
Thanks guys for the input.The responses were very confirming.I have removed this panel already.I informed the customer of the huge danger I felt about the situation and then began the demolition.I just wanted to make sure I wasnt out of my mind...forgeting some extraneous code about equipment fed from more than one source with parallel feeders or some such thing.But...I guess Im not as dumb as I thought I was.
 
Jesse,

Removing the sub-panel is a Good decision!

The potential for Back Feeding is Deadly Dangerous!

Results like this thread make the forum very useful.
 
I came upon a job recently where the electrician needed to install a 200 Amp 3 phase subpanel.So he grabbed 100 Amps from each of 2 seperate 3 phase panels which are side by side,but on 2 differant meters.

An electrician did not do that. He may have fancied himself an electrician, but most assuredly he was not.
 