I agree. Have you seen the cost of these? (I haven't).Seems like there are only 4 sizes, would be good product to carry on truck
Why wouldn't they be treated like wire-nuts?Looks like an Isco ad picture I don't see mounting screws in the boxes. These MAC connectors will trip up inspectors
I get that. Alumiconns come with three ports, too, which is what I used on my bike for direct power to relays.Because they are set screw connectors ie like a lug. The basic rule is one wire per lug
I can see how this would work for stranded conductors. But it seems to me that with solid conductors of varying sizes, it's possible to come up with a geometry where one of the conductors is loose. I'm really curious to see what the hole looks like in that lug.Noted Ilsco has a new insulated splice connector that is rated for multiple wire sizes in one lug.
Because they are set screw connectors ie like a lug. The basic rule is one wire per lug
But up to four of different sizes? I thought the most was two of the same size.UL Recognized 'rail mounted terminal strips' have allowed multiple conductors per set screw opening for years. Maybe UL has changed/harmonized some of their listing requirements?
I looked up the catalog sheet out of curiosity ... https://commerce.ilsco.com/documents/PDF/TechnicalDrawing/MAC.pdf and find it clearly confusing ... #6 to #18 solid CU, #6 to #12 AL ... probably because #12 AL is the smallest size?, and #6-#14 stranded. This assumes they mean stranded by FLEX.I can see how this would work for stranded conductors. But it seems to me that with solid conductors of varying sizes, it's possible to come up with a geometry where one of the conductors is loose.
Since the purpose of this device is for splicing copper to aluminum, I think it's clear that the aluminum is to be in one port, and the copper is to be in the other, not "mix and match."but AL and CU in the same port is not allowed.
No, they mean finely stranded like DLO. Their literature include a table describing the allowable number of strands. There's also a chart listing every combination of solid and stranded allowed in one hole. With a finely stranded conductor, it's just one conductor per hole.This assumes they mean stranded by FLEX.
I can see how this would work for stranded conductors. But it seems to me that with solid conductors of varying sizes, it's possible to come up with a geometry where one of the conductors is loose. I'm really curious to see what the hole looks like in that lug.
My point is, that at least with stranded conductors, the wire strands can move to conform to the space as the lug screw is tightened. Now imagine 3 solid #10 conductors and a solid #12. in a single port. It seems that such a configuration could easily leave the #12 loose.Explain how a set screw lug EVER puts even pressure on all strands. It never does. That’s part of why the failure rates are so high.