From the ROP for the change to the table, note the bold which not mine-but part of the proposal.
http://www.nfpa.org/assets/files/AboutTheCodes/70/70-A2010-ROP.pdf
Affirmative: 11
_______________________________________________________________
6-57 Log #635 NEC-P06
Final Action: Accept
(Table 310.15(B)(2)(a))
Submitter:
James M. Daly, Rep. NEC/CEC Ampacity Harmonization Task
Group
Recommendation:
Revise first column heading in Table 310.15(B)(2)(a) from
?Number of Current-Carrying Conductors? to ?Number of Conductors (See
Note 1.)?.
Add a Note below the Table before FPN No. 1 to read:
1
Number of Conductors is the total number of conductors in the raceway or
cable adjusted in accordance with 310.15(B)(4) and (5).
Substantiation:
A companion proposal is being submitted for Table B.310.11.
This Table was originally added to the Code in 1940 and the column
heading remained as ?Number of Conductors? until 1993. During the 1993
NEC revision cycle, the column headings in Table 310.15(B)(2)(a) and
Table B.310.11 were editorially changed to ?Number of Current-Carrying
Conductors?. There was no Proposal, Comment, or Panel Action to make the
change. A chronological history of the changes in the Tables is attached for
reference.
This reinstatement of the original column heading permits the user to take
the total number of conductors in the cable or raceway and subtract the neutral
conductors not required to be counted under 310.15(B)(4) and the grounding or
bonding conductors not required to be counted under 310.15(B)(5). The result
is the number of conductors that
may be simultaneously energized and this
number would be used to select the adjustment factor from the Table.
The Note is proposed for clarity since there has been some confusion that the
column referred to the total number of conductors in the raceway or cable.
The correction to the column heading also correlates with the column
headings in Table 400.5 in the NEC and Table 5C in the 2006 Canadian
Electrical Code, Part I.