Granted... but the Code does not always match the physics of the phenomena or the level of detail. We could have derating of power conductors by single increment rather than stages... but we don't. And more to the point of this topic, the conductors are not control wires.If that were relevant, then the code would make us count control wires when we decide whether to derate. But it doesn't. 310.15(B)(2)(a), Exception 1. I can put a 3-phase branch circuit (3-CCCs) in a conduit, and then fill the conduit to 40% with control wires, and not have to derate.
So whichever side of the coin suits your purpose is the one you use?The code, as written, does support my viewpoint. :happyyes:
A conductor that cannot carry current because it is physically disconnected, and cannot be connected, is not a CCC. The NEC does not specifically define "current carrying conductor," but I think it fair to say that that term can be defined as a conductor that carries, or that at least has the possibility of carrying, current. I see this situation as being vastly different from having two single-phase circuits, one serving lights and the other receptacles, sharing a conduit. It is physically possible for both the lights and something plugged into the receptacle to be both carrying current at the same time. So even if there is nothing (at the present moment) plugged into the receptacle, the conduit still gets counted as having 4 CCCs. In the present installation, an interlock physically prevents both sets of conductors from being connected at the same time. The ones that are not connected are, by definition of CCC, not CCCs. Therefore, you don't get to read any deeper into the requirements of 310.15(B)(3)(a) than to recognize that the article does not apply because you don't have more than three CCCs.
I agree with your "not connected" premise. IMO, however, the premise fails for this instance because the conductors are still physically connected to electrical equipment.
Also, the interlock is not adequate justification by itself. What if these conductors powered short-cycle jogging motors, with large starting current, the conductors temperature could potentially reach their thermal limit... yet they were never coincidental loads.
Don't get me wrong. I'm all for not counting conductors as ccc's when they shouldn't be counted. :happyyes: