I've been taking pictures of these whenever I see them. Unfortunately nothing real ridiculous, although that one appears to be real low because its down and embankment a bit. All autos probably?
 

Attachments

  • 20170206_114923_resized.jpg
    20170206_114923_resized.jpg
    136.6 KB · Views: 2
  • 20170208_093010_resized.jpg
    20170208_093010_resized.jpg
    137.1 KB · Views: 2
  • 20170211_165218_resized.jpg
    20170211_165218_resized.jpg
    79.8 KB · Views: 2
  • 20170214_135020_resized.jpg
    20170214_135020_resized.jpg
    120.5 KB · Views: 2
  • 20170218_121124_resized.jpg
    20170218_121124_resized.jpg
    148.6 KB · Views: 2
Number 1 looks like an open delta, while number four, with mismatched sizes might, maybe, be a high leg? Or just what they had sitting around?
I can't really see the secondary conductors.
 
1 and 2 are 32 step voltage regulators, while 3 and 5 appear to be 2 winding isolation with a secondary 5kv and below. #4 looks like a step down with a delta secondary, but the image is not 100% telling.
 
Number 1 looks like an open delta, while number four, with mismatched sizes might, maybe, be a high leg? Or just what they had sitting around?
I can't really see the secondary conductors.

I am guessing #1 is also open delta since all the phases are tapped but only 2 reg cans, in addition to what looks like no primary neutral on the pole to the left.
 
Anyone care to take a guess on this “accessory”

Paint%20job_zpscyiqo3ol.jpg
 
1 & 2 are automatic voltage regs. 3, 4, & 5 are most likley wye/delta banks. It looks like #4 is hooked up wye/delta; probably feeding an old 2400 or 4800 volt system. I find it odd that #1 only has voltage correction on 2 phases, if you look closely you can see (or not see, hehe) no insulator on the center phase.

Sent from my VS987 using Tapatalk
 
Last edited:
You people are sick...

:rant::p:lol::lol::lol::lol::thumbsup:

Trust me, its the tip of the iceburg. At least for me anyway :lol: I photograph street lights just because I like how they look, and all the different models out there.
 
1 & 2 are automatic voltage regs. 3, 4, & 5 are most likley wye/delta banks. It looks like #4 is hooked up wye/delta; probably feeding an old 2400 or 4800 volt system. I find it odd that #1 only has voltage correction on 2 phases, if you look closely you can see (or not see, hehe) no insulator on the center phase.

Sent from my VS987 using Tapatalk

Yup, open delta correction. Common on pure 3 wire circuits because it requires only two regs instead of 3.


See pages 4 and 5 for the various connection types:


http://www.cooperindustries.com/con.../library/225_VoltageRegulators/MN225008EN.pdf
 
Interesting. That's something new, thank you for the documentation. When we build a regulator bank we never hook them up in open delta, its either 3 for 3 phase or 1 for single.

Sent from my VS987 using Tapatalk

Id guess because your system is 4 wire wye, which mandates 3 regs if you want all 3 phases to have the correct voltage.
 
Id guess because your system is 4 wire wye, which mandates 3 regs if you want all 3 phases to have the correct voltage.
Most of our network is 4w wye. We have a lot of delta too. My coverage area actually more delta than wye, very rural and long runs. Still; using 2 regs in an open delta is something I've never done.

Sent from my VS987 using Tapatalk
 
Most of our network is 4w wye. We have a lot of delta too. My coverage area actually more delta than wye, very rural and long runs. Still; using 2 regs in an open delta is something I've never done.

Sent from my VS987 using Tapatalk

Never say never, it might be tomorrow where an open delta is required :p
 