- Windsor, CO NEC: 2023
- Hospital Master Electrician
How do you go about changing the manual of style?
My motives are as follows. I thought this was enough of a divergence that it warranted it's own topic. In the (now becoming infamous) undercabinet thread, Mike posted the following:
For the record, I flatly disbelieve that 640.21(E) was intended to permit a cord to be permanently connected to premises wiring. But, the way it is worded, in combination with the beginning of the Article, it can be read that way.
In NEC-2002, Article 527 (NEC-2005 Article 590) sets the tone for this concept, because that's what the entire article is about. Unfortunately, this tone isn't that hot either.
In general, the NEC does not seem to give due credit to how profound these huge exceptions can be, and how profoundly different the same section can be interpreted. So, some sort of master key seems to be the answer, in my mind. Something that says, This section supercedes what you know about that other section. Something brief, but clear that when you see that key, you know the order of things.
Sorry for (my typical) long post, but I am very interested to hear other's opinions on this.
[ May 07, 2005, 08:14 AM: Message edited by: georgestolz ]
While my initial reaction was disbelief, upon closer review, I discovered his basic interpretation was valid.Originally posted by jwelectric:
In 400.8 (1) we are told that a flexible cord can not be used as a substitute for fixed wiring. Then it would seem that in order to install this permanently installed audio appliance we are required to use a plug and receptacle except 640.21 allows us the relief to bypass this plug that would other wise be required to be installed in series with the equipment. The phrase ?direct connection? mentioned in 640.21 clearly states that we are not required to install a disconnect (plug) in series with this hard wired flexible cord to a permanently installed appliance. This has the same meaning as the series over current device mentioned in 695.4 (B) (1).
640.9 Wiring Methods.
(A) Wiring to and Between Audio Equipment.
(1) Power Wiring. Wiring and equipment from source of power to and between devices connected to the premises wiring systems shall comply with the requirements of Chapters 1 through 4, except as modified by this article.
Essentially, what I am getting at is that there needs to be a sweeping change in the way the NEC deals with superceding rules. Perhaps I just need a better understanding, and in the course of time someone is going to clarify the "chain of command" in this matter. As it stands, as a user of the NEC (pretty good at it sometimes), this chain is unclear.620.21(E) Between Equipment Racks and Premises Wiring System. Flexible cords and cables shall be permitted for the electrical connection of permanently installed equipment racks to the premises wiring system to facilitate access to equipment or for the purpose of isolating the technical power system of the rack from the premises ground. Connection shall be made either using approved plugs and receptacles or by direct connection within an approved enclosure. Flexible cords and cables shall not be subjected to physical manipulation or abuse while the rack is in use.
527.2(A) makes a sweeping statement about the whole article, and then it's assumed that 527.4(B) is saying, 240 applies except for this and this and this.527.4 General.
(A) Services. Services shall be installed in conformance with Article 230.
(B) Feeders. Feeders shall be protected as provided in Article 240. They shall originate in an approved distribution center. Conductors shall be permitted within cable assemblies or within multiconductor cords or cables of a type identified in Table 400.4 for hard usage or extra-hard usage. For the purpose of this section, Type NM and Type NMC cables shall be permitted to be used in any dwelling, building, or structure without any height limitation. permitted.