surgegs430
Member
- Location
 - california
 
SO I CANT FIGURE WHAT SIZE BREAKER TO USE FOR MY INSTALL, HERES WHAT I GOT ITS A 3.7 HP SINGLE PHASE 230V WITH FULLY LOAD AMP 17.2A AND ITS CONTINOUS. I WNET TO 310.15(B)(16) THHN FOR MY WIRE SIZE 125%X FLA=21.625 SO THEREFORE I CAN GET AWAY WITH A COPPER 12AWG BUT I GOT 10"S IN THE CONDUIT ALREADY NOW I FIGURE WHY NOT A 2POLE 30A BREAKER BUT I LOOK INTO IT AND 430.52 MAXIMUM RATING MOTOR BRANCH CIRCUIT 250%XFLA= 43.25A SO NOW I WOULD GO WITH A 2POLE 50A NOW IM NOT SURE WHICH ROUTE TO TAKE DO I PUT A 2POLE 50A WITH #8"S OR CAN I GET AWAY WITH 2POLE 30A & #10"S
	
		
			
		
		
	
				
			
				