Hello everyone,
New to the forum, but I could use any and all input. I have a 5hp AHU controlled by a VSD controller, 3ph/480v, FLA 7.6A. The contractor has installed a 3-pole/50amp and the conductors feeding the controller are #10 THHN awg. The contractor and even MEP rep says this is fine, due to not wanting start-up and in-rush current to trip the breaker. I realize that OCP has to be sized at 125% and even 175% on occasion depending on other factors, but in no case due any of my calculations allow for a 50 amp breaker to protect #10 wire. Am I getting this wrong? They also have an OAHU VSD fed with a 70 amp and #8awg. I've got them on warranty no matter what because the as-builts show these to be a 30 amp and a 50 amp respectively, but I'd still like to know exactly what the NEC allows as far as overprotecting conductors in this manner. Any help would be appreciated an this.
New to the forum, but I could use any and all input. I have a 5hp AHU controlled by a VSD controller, 3ph/480v, FLA 7.6A. The contractor has installed a 3-pole/50amp and the conductors feeding the controller are #10 THHN awg. The contractor and even MEP rep says this is fine, due to not wanting start-up and in-rush current to trip the breaker. I realize that OCP has to be sized at 125% and even 175% on occasion depending on other factors, but in no case due any of my calculations allow for a 50 amp breaker to protect #10 wire. Am I getting this wrong? They also have an OAHU VSD fed with a 70 amp and #8awg. I've got them on warranty no matter what because the as-builts show these to be a 30 amp and a 50 amp respectively, but I'd still like to know exactly what the NEC allows as far as overprotecting conductors in this manner. Any help would be appreciated an this.