At the large place that I retired from they had over 500 VFD'S from 2 to 1,750 HP. Not one drive had shielded cable from the drive to the motor. Almost every drive was within 50' from the motor. All had line side reactors. All wires were in EMT and meta! flex ( sealtite or greenfield ) and copper ground wire from drive to motors. I believe that for normal applications the shielded cable is not necessary & a waste of money. I asked service tech from two drive companies and they said the same thing. In a new building every drive 40 HP & larger were 18 pulse w/o shielded cable. Some of the drives fed plain Jane NEMA frame three phase motors that were over 30 years old and drives had over 120,000 hours of running time.