We have a 20 HP 460 VAC motor. FLA: 24 Amps. RPM: 1765. Des. B
We need to determine what will be the corrcect type and size breaker for this motor.
The old 30 Amp 3 Pole ITE Cat.# ED63A030 Instantaneous Magnetic Trip Breaker does not hold the motor. Keeps tripping. We meggered the motor and verified all of the electrical connections are tight. Nothing wrong in the field. We think that this old ITE Breaker is the wrong type.
Mag only (instantaneous) CB shall part of a listed combination (CB contactor, overloads) starter. They work just fine. In fact that's my preference. Only you can look at the bucket and see if it is a listed combination starter. If it is not, then someone has wrongly installed the CB - I can't help and none of this applies.
Assumption: The CB is tripping on motor start.
So, did the old CB hold the starting current some time in the past and now does not? Or is this the first time the CB has been installed in this service?
All instantaneous CBs have adjustment dials. (note to nit pickers: Yes, I'm sure you can find plenty of screwy exceptions that don't fit the OP). The CB may say 30A on the handle (or nameplate), but the instantaneous rating will be maybe 100A to 500A (this is a guess) - dial setable. That's right, the nameplate may say 30A, and the CB will hold in forever at 500A.
For your example, I expect a setting of 200A to 300A. Look at (2011) 430.52.3. Read all of exceptions. If the CB is set below this level, set it up -
Per the NEC 430.52.3
If it has held in the past, is set correctly, and now does not hold starting current, replace it with the same spec CB - and set it correctly.
If you can, get a recording meter and check the starting current. "Instantaneous" means just that - one cycle is enough. The instantaneous dials have to be set above the peak current.