mstrlucky74
- NJ
I have no idea what this means. Maybe some context will help.... I understand it’s either continuous duty or duty cycle and not continuous load.
Start with 430.6A. If it this standard stuff, conductor ampacity, switch ratings, short circuit, ground fault, is per the tables.If given the HP and FLA you would size conductor based on FLA X 125% and not HP and go to NEC? ....
On a side note this feed is from MCC to VFD then to motor. How would one know if neutral and/or EGG is required? RGS conduit. I would think just 3 phases and a separate ground. Thanks.
Although technically allowable per the NEC, you would NOT use only the conduit as the EGC for a VFD circuit unless you are a glutton for punishment. Even in metal conduit you always run a separate ground wire from the motor frame to the VFD ground terminal, not to a ground lug in the box or panel. Then the VFD is connected to ground as well using a different ground terminal, which is why VFDs will always have two ground terminals; one for the motor ground, one for the system ground....Metal raceways can be the EGC nearly all cases as well (outside of specifications exceeding code anyway).
For the input wiring. Output wire from the VFD to the motor is per the NEC tables.Good to know. That is sort of important. Did you look at 430 Part X, Adjustable Speed Drive Systems?
430.122 changes the conductor sizing to 125% of the rated input current to the drive - not the table motor FLC.
TY!!Neutral not likely needed. May not even be present in the MCC.
EGC is nearly always required for anything over 50 volts. Metal raceways can be the EGC nearly all cases as well (outside of specifications exceeding code anyway).
TY!! I see that. So do you still add 125% to nameplate(FLA) if it's continuous?For conductor sizing you should use Tables 430.250 which happens to be the same as the nameplate
For conductor size you add 125%TY!! I see that. So do you still add 125% to nameplate(FLA) if it's continuous?
430.22 Single Motor. Conductors that supply a single motor
used in a continuous duty application shall have an ampacity of
not less than 125 percent of the motor full-load current rating,
as determined by 430.6(A)(1), or not less than specified in
430.22(A) through (G).
NEC grounding requirements are for safety, VFD grounding requirements are for electrical noise abatement. Ignore at your own risk.
As said by iceworm, RTFM; Read the FACTORY Manual...