If you have a branch circuit, then the GFSC protection must be sized as required for branch circuits. Which means, per the section you previously mentioned, sized for the smallest motor.My thought is it should be sized as a feeder for GFSC since the circuit feeds two separate motor starters as opposed to sizing it for the smallest motor. But I don’t believe you then need to run individual branch circuits.