If I have a ? HP 120V motor with thermal protection built in can I consider this thermal overload as all the OL needed/required?
In this example if I understand 430 correctly my circuit will include:
40A 1P circuit breaker (13.8x250%) ? 430-52
#14cu THHN (13.8x125%) ? 430-22(A)
30A non-fused disconnect (13.8x115%) ? 430-110(A)
Is this example correct?
Does anyone have a good website or resource about motor circuiting?
In this example if I understand 430 correctly my circuit will include:
40A 1P circuit breaker (13.8x250%) ? 430-52
#14cu THHN (13.8x125%) ? 430-22(A)
30A non-fused disconnect (13.8x115%) ? 430-110(A)
Is this example correct?
Does anyone have a good website or resource about motor circuiting?