In a motor controller we have (230/3/60) a 2 HP(6.8 FLA) motor and a 1/2 HP (2.2 FLA). For breaker sizing we use table 430.52.
2HP 6.8 * 2.50 = 17 or a 15 amp breaker (next lowest size.)
1/2 HP 2.2 * 2.50 = 5.5 or a 5 amp breaker.
OR does exception # 2 from 430.52 (C) (3) mean if the FLA is 8 or less we can use a 15 amp circuit breaker or does we still use the 250% rule? Is a 15 amp the minimum "standard" size?
Thanks!
Thanks!