Even more interesting. I checked the two references. Neither mentions (or aludes to) anything about motor windings having a Negative Temperature Cooeficient. I'm not sure why you cited them. All of the data/equations are consistant with the Copper PTC that has been known for perhaps the last 250? years....in our lab we actually witnessed that a lot of large frame motors, i.e. over 10HP 460V, actually exhibited Negative Coefficient of Resistance properties...
Perhaps I don't understand your definition of NTC.
Are you saying the winding resistance goes down with increasing temp?
Are you saying the LRC goes up with increasing temp?
Is there some other measurement you are using to infer this NTC?
I am. There is no known physics that will make copper winding resistance go down with incresaing temp? Jim - you already knew that.I am not surprised that you have seen motors exhibit an NTC. For many analysis a motor is a transformer that has a moving secondary. Transformer damage curves are often published with two curves; one for cold energization and one for hot.
carl