They do make those. They are called "
Motor Protection Circuit Breakers" (MPCB). Not all of the mfrs have them, but most do. UL only recently started allowing them to be called "Circuit Breakers" however, because the UL standard for "circuit breakers", UL489, did not allow for adjustable thermal elements. So up until then they had to be called "Manual Motor Starters" and were listed under UL508 as a motor circuit component, meaning technically, you STILL had to have a CB or fuses ahead of them. Once UL caved and allowed this "new" category of MPCBs, it allows you to have it all in one device. The concept has not yet caught on in a big way though, people don't like change...
By the way, they don't make them that have 20x adjustments to the mag trips though, because the breakers themselves have a 10x limit to what they can handle from a mechanical forces standpoint. Even if you buy a "Molded Case Switch", which is a circuit breaker without "any" trip elements, it technically still has one, factory set for 10x the rating and not adjustable, because that's the mechanical limit of the breaker mechanism itself.