petersonra
- Northern illinois
- Semi-retired engineer
Are motor circuit conductors not part of a branch circuit and thus covered in art 220?
While I could argue that premise, let's set that aside for now.Smart$,
The scope of Article 210 specifically excludes motor circuits unless part of a combination circuit.
So what about this scenario where the control circuit conductors originate from the same system, such as from a 208V motor starter with 120V control taken directly from the feeder (i.e. no control transformer)???I don't necessarily agree with Don's argument, but I see where he is coming from. The last paragraph of 310.15(B)(3)(a) used to be an exception, now it is a paragraph within the general rule. I think the intent is to include all power and lighting circuits, including motor circuit conductors.
That section has nothing to do with the motor circuit conductor size....
How do you get around 220.14(C)??? ...
That is correct, but irrelevant to matter.That section has nothing to do with the motor circuit conductor size.
Ahh, I see!!! That'll take a bit more thought and investigation on my part.Smart$,
I think power circuits for motors are required to be derated. I can't prove that you are not required to include motor control circuits as current carrying conductors where not part of a "separate system".
Smart$,
I found the language relating to "different systems" all the way back to the 1947 Code. Rule 3011 of the 1947 Code listed many
other system conductors that were permitted to be installed in the same raceway with power and light conductors, not just AC and DC.
I found the exception that permitted conductors of different systems to be excluded from derating as far back as 1959.
Ultimately, derating is intended to apply to power and lighting circuits only (including motor circuits). The reference to "different systems"
doesn't really fit in the modern context of the Code.
I think the wording should be changed to, in effect, say conductors which contribute very little heat. Or better yet, remove the paragraph entirely, and spell out additional current-carrying conductors which are permitted to not be counted as a CCC. We already have neutral and grounding conductors. Add certain control conductors, and perhaps multiple conductors which originate from one (not taps) such as multiple lighting switch legs and travelers. It's just common sense backed up by physics!!!Does a conductor carrying say 10 amps for a motor produce any more or less heat within a raceway than the same size conductor carrying 10 amps for a resistive load? That is what the derating is supposed to be about is to keep heating effects under control.
Maybe it is not written correctly, and I am having a little bit of a hard time trying to see what some of you are seeing, but I think it is intended that all "current carrying" conductors be included for number of current carrying conductors in a raceway. A motor circuit conductor is a current carrying conductor unless it qualifies as a neutral that only carries unbalanced current in a multiwire branch circuit.
If you don't think motor conductors produce heat I can show you a few that obviously do, and they are sized according to the deration factors in 310.15 - the raceways still do warm up enough you don't need instruments to tell.
There is no question that the motor conductors produce heat just like any other current carrying conductor.Does a conductor carrying say 10 amps for a motor produce any more or less heat within a raceway than the same size conductor carrying 10 amps for a resistive load? That is what the derating is supposed to be about is to keep heating effects under control.
So the wording leaves the rationale irreproachable? How is having [SDS] control conductors in the same conduit going to reduce the amount of I?R heat, compared to a similar scenario where the control conductors are run separately? That is, conduit run with control conductors and more than three motor circuit conductors requires no derating, versus a conduit run just with more than three motor circuit conductors does require derating...? I must say, that's defies the logic and purpose of derating.There is no question that the motor conductors produce heat just like any other current carrying conductor.
That being said, ...the code wording does not require ...motor circuit conductors be derated. ... The ...motor circuit conductors are already derated to 80% based on the rules in Article 430.
Only continuous load motors - which in general we treat most of them as though they are continuous load, same basic rule, different code section applies to conductors for other continuous loads.The other issue is the fact that the motor circuit conductors are already derated to 80% based on the rules in Article 430.
Sure it defies logic, but I have never said that the code is logical. Of course the motor conductors make heat and have the same heating issues as any other current carrying conductor, but, in my opinion, under the conditions given in my original post, the code does not require those conductors to be derated. If I remember, I will submit a proposal to delete the article reference at the end of this section for the 2017 code. If that is no longer there, then I think that motor conductors would be power conductors for the purposes of derating.So the wording leaves the rationale irreproachable? How is having [SDS] control conductors in the same conduit going to reduce the amount of I?R heat, compared to a similar scenario where the control conductors are run separately? That is, conduit run with control conductors and more than three motor circuit conductors requires no derating, versus a conduit run just with more than three motor circuit conductors does require derating...? I must say, that's defies the logic and purpose of derating.
I think you are correct.Now you have me wondering how 110.14(C) terminal temperature limitations applies to Article 430 motor circuit conductor ampacity. Chapter 2 continuous load conductors must also have an ampacity of 125% of the calculated load current... but we are permitted to use the conductor ampacity rating before adjustment and correction, i.e. the higher temperature Table value (e.g. 90?C rating) [210.19(A)(1)]. There is no such clause in Article 430 (that I'm aware of). Are we permitted to determine 125% rating from the higher temperature-rating value? If so, where is that stated in Article 430. If not stated anywhere, the 125% ampacity seems to have to be based on the termination temperature limitation ampacity...??????