This one is puzzling me.
I need to install a 115VAC branch circuit for some machinery. Here are the requirements and background info:
1. The building was spec'd by the GC to have three machines on this single branch circuit, with only one to be operated at a time.
2. Each machine has a momentary push-button switch to energize the motor. The motor would only be energized for a short period of time (45-50 sec) with long set-up times between operations (very low duty-cycle).
3. The motors are rated as follows: 1HP, 1 PH, FLA=11.2, 115V/60Hz, SF=1.6, SFA=15.0, Duty=5 Min.
4. Each motor's control box is factory-wired with a flexible 14AWG power cord that ends in a standard Type-B grounded plug.
5. I contacted the machines' manufacturer and spoke with their technical service dept. They recommended a 25A or 30A branch circuit (they said that when they do the installations, they typically use 30A breakers).
Calculations & Questions:
1. Conductors:
Going through the NEC, it appears that 430.22(E) would apply. The
examples they give for "Classification of Service" are rather limited and
appear highly specialized. I'm guessing that my application would be classified as "Intermittent Duty". Does this seem right? If so, then my conductors shall have an ampacity of not less than 85% of the motor's nameplate current rating.
But which nameplate current rating do I use (FLA or SFA)? I'm going to assume I use the FLA. Then my conductors should be sized not less than:
11.2A * 85% = 9.52A
(I suppose this is how they are able to put a 14AWG cord on the motor.)
Since we'll have three machines on this branch circuit, then 430.24 applies. And for intermittent duty, then Exception 1 applies. So:
Sum = 9.52A + 9.52A + 9.52A = 28.56A
So that would mean a 30A breaker and 10AWG conductors from the distribution panel to the outlets are called for. Does this all seem correct?
2. Motor & Branch Circuit Overload Protection
For intermittent duty motors, I can apply 430.33: "...shall be permitted to be protected against overload by the branch-circuit short-circuit and ground-fault protective device, provided the protective device rating does not exceed that specified in Table 430.52."
From Table 430.52:
11.2A * 300% = 33.6A (Again I'm using the FLA rating)
So a 30A breaker satisfies this requirement. Everything look good so far?
3. Motor Branch Circuit Short-Circuit & Ground-Fault Protection
This is where I start to get confused. According to 430.53(A), two or more motors (not over 1 HP) shall be permitted on a nominal 120-volt branch circuit protected at not over 20A.
So how do we reconcile this 20A limitation with the requirement for a 30A breaker?
4. Plugs & Receptacles
As I mentioned, the power cords for these machines all have Type-B plugs. Is it Ok to put three 20A receptacles on this 30A branch, one to feed each machine? I've never seen a NEMA 5-15 outlet rated to carry 30A.
And what about GFCI? When I called the manufacturer's tech support, the guy there had never heard of GFCI on any installations of these machines. If GFCI is required, would I again use a 20A rated device?
Thanks again in advance for ANY assistance!
confused:
1. Conductors:
11.2A * 85% = 9.52A
From Table 430.52:
confused: