I would like the opinion of the all and powerful form
I had a question on a test that was worded as follows:
"What is the Maximum size Dual Element (time-Delay) fuse that can be used to protect a three-phase 40hp motor at 460V?"
A)175 amp
B)100 amp
C)125 amp
D)150 amp
The answer I chose was "C" and I got there this way:
T430.250 Full load current = 52 amps
looking at table 430.52 I should multiply 52 x 175% but the question ask for the "Maximum size" so I look at 430.52 Exception #2(b) and it allows me to multiply 52 x 225% and come up with 117 amps and 240.6 allows me to upsize to 125 amp fuse. I was told I was wrong.....
The answer was suppose to be "B" and the math worked out like this:
T430.250 Full load amps = 52 amps
52 x 175%(T430.52) = 91 amps
240.6 upsize to 100 amp fuse
If I use a 100 amp fuse and the motor does not start would I not have to use a larger fuse up to a 225%??? How would you have answered this question??
Thanks,
Kevin
I had a question on a test that was worded as follows:
"What is the Maximum size Dual Element (time-Delay) fuse that can be used to protect a three-phase 40hp motor at 460V?"
A)175 amp
B)100 amp
C)125 amp
D)150 amp
The answer I chose was "C" and I got there this way:
T430.250 Full load current = 52 amps
looking at table 430.52 I should multiply 52 x 175% but the question ask for the "Maximum size" so I look at 430.52 Exception #2(b) and it allows me to multiply 52 x 225% and come up with 117 amps and 240.6 allows me to upsize to 125 amp fuse. I was told I was wrong.....
The answer was suppose to be "B" and the math worked out like this:
T430.250 Full load amps = 52 amps
52 x 175%(T430.52) = 91 amps
240.6 upsize to 100 amp fuse
If I use a 100 amp fuse and the motor does not start would I not have to use a larger fuse up to a 225%??? How would you have answered this question??
Thanks,
Kevin