a 3hp single phase motor will not start the same compressor as easily as a three phase motor, especially a 480 volt one.
Common misconception. Torque is torque is torque. HP is torque at speed. It’s no different.a 3hp single phase motor will not start the same compressor as easily as a three phase motor, especially a 480 volt one.
The breaker up size does not require an increase in BC ampacity.Feeder and branch wire gauge should be checked, too. If the breaker wasn't upsized, the wiring might not have been either.
Provided the circuit breaker is not used for OL protection also.The breaker up size does not require an increase in BC ampacity.
Provided the circuit breaker is not used for OL protection also.
Common misconception. Torque is torque is torque. HP is torque at speed. It’s no different.
did they change the supply voltage to 240?The panel is an old FPE, Breaker is two pole 20 wire is #12 I actually didn't do the hook up another electrician did and I'm just trouble shooting it for the owner. It used to be a 480 volt 3 phase compressor that they changed out to a 240 volt single phase motor.
250% still gives you max SCGFP of 15.Yeah, OK, didn't think that through...
But we don't know what was there. Being 480V it might have had its own local combo starter with an OL relay so the 20A was just the feeder protection for #12 wires.
most general purpose induction motors particularly in ~1800 RPM version will have similar enough characteristics they are usually interchangeable though. Main thing is if it has enough torque to start accelerating the load or not. Once it starts accelerating the single phase version possibly takes longer to reach full speed but it usually can do it.While that’s true, different types of motors of the same HP can have drastically different starting torques.
If almost everything else is the same the starting Torque should be the same. The main difference you will notice between a single phase motor and a three phase is the efficiency and power factor are Usually much better on a three phase motor.a 3hp single phase motor will not start the same compressor as easily as a three phase motor, especially a 480 volt one.
I don't know about that. I often see single phase motors with high power factor marked on nameplate compared to a three phase motor of similar design.If almost everything else is the same the starting Torque should be the same. The main difference you will notice between a single phase motor and a three phase is the efficiency and power factor are Usually much better on a three phase motor.
most general purpose induction motors particularly in ~1800 RPM version will have similar enough characteristics they are usually interchangeable though. Main thing is if it has enough torque to start accelerating the load or not. Once it starts accelerating the single phase version possibly takes longer to reach full speed but it usually can do it.
Note the OP said at start. Not much torque at zero speed.Common misconception. Torque is torque is torque. HP is torque at speed. It’s no different.
Just an observation on my part if you look at most single phase motors. They're in the low 80% efficiency and PF. Most all newer 3 PH motors are around 90-92%I don't know about that. I often see single phase motors with high power factor marked on nameplate compared to a three phase motor of similar design.
Well there was mention of the item originally having a three phase motor on it, which majority of those are induction motors, particularly in the under 100 HP ranges.With the specific example in the OP, I agree. But there are a lot of motor types with either very high or very low starting torques.
DC series-wound vs shaded pole, are extreme examples.
The post I was replying to didn’t limit the motor type.
Well don't you need torque to break free from standstill? Single phase motor with open aux/start winding or three phase motor with "lost phase" would have no torque if rotor is not turning at all, if rotor is turning it may continue to turn unless the connected load demands more torque than is being produced.Note the OP said at start. Not much torque at zero speed.
Note the OP said at start. Not much torque at zero speed.
There are a few approaches to troubleshooting. The first one is a process of elimination. The simplest advice I can give without any further knowledge other than what you have discussed. Is to drop the load (the motor) then allow the motor contactor via HOA switch to energize the coil of the motor starter. If it starts under normal operation then there's a possiblity you could have an issue with the motor itself. You would need to meg the motor with a digital mulitmeter or DMM. Fluke and a bunch of other manufacturers make specific meters for megging motors, either digital or analog meters. I always use a Fluke 1587, which has never failed me. When ever you start a high inductive load, you will see an inrush current. It settles down shortly after and runs at the FLA/FLC of the motor nameplate.I have a 3 HP motor that is 12.6 amps. I put my clamp meter on the wires at the breaker and at start up it draws 71 amps is that normal? It trips the breaker in about 3 seconds. I don't have much experience with motor circuits. What can I do to correct this?