Hello guys, I have a question and I hope you can help me, when you are selecting your wires for a motor circuit, you select it by 1.25 of table 430.250.
When you calculate feeders or branch circuits you use 125% of continuous current plus 100% of non continuous or conditions of use (adjustment and/or correction factors), whichever is higher.
The question is: It is the same for motors circuits? the higher of 430.250 *1.25 or adjustment and correction factors? or you have to apply both? continuous and correction?
In a totally unrelated question, I have seen in a lot of mining projects that the steel structure of pretty much everything gets connected to ground (4/0 wire) and they connect the panelboards to ground too.
It is NEC complaint to connect the panel boards to this ground when the feeder already has an EGC? I would say no because that would create parallel ways for the fault current and besides 250.4 (A) (5) says that "The earth shall not be considered as an effective ground-fault current path". What do you think?
Tom
When you calculate feeders or branch circuits you use 125% of continuous current plus 100% of non continuous or conditions of use (adjustment and/or correction factors), whichever is higher.
The question is: It is the same for motors circuits? the higher of 430.250 *1.25 or adjustment and correction factors? or you have to apply both? continuous and correction?
In a totally unrelated question, I have seen in a lot of mining projects that the steel structure of pretty much everything gets connected to ground (4/0 wire) and they connect the panelboards to ground too.
It is NEC complaint to connect the panel boards to this ground when the feeder already has an EGC? I would say no because that would create parallel ways for the fault current and besides 250.4 (A) (5) says that "The earth shall not be considered as an effective ground-fault current path". What do you think?