Device is rated to carry 15 or 30 amps.
i believe u mean continuous current rating of the device?
Yes. It is not a circuit breaker, it is a 15 or 30 amp switch with magnetic trip but no thermal trip function. The 15 amp device only went down to 45 magnetic trip setting - but if you continuously loaded it to 30 amps it won't trip even though it is more than it is continuously rated for.Device is rated to carry 15 or 30 amps.
i believe u mean continuous current rating of the device?
Yes. It is not a circuit breaker, it is a 15 or 30 amp switch with magnetic trip but no thermal trip function.
:ashamed1: yep - instantaneous trip breaker, should have been more clear - is not a thermal magnetic breaker like most panelboard breakers usually are, and is for the most part only for motor applications.That would be a circuit breaker, by definition.
250% for a inverse time breaker, and if that won't let the motor start there is allowances to go higher. Instantaneous trip breakers can be 800% or 1100% for design B motors.The previous posters are correct - those amp values are continuous current ratings. The question then is - why would I ever want to buy a breaker that's rated higher than the FLA of the motor, would that be a waste of money? The answer is no. These new high efficiency motors that are being built nowadays have higher inrush values. You can run into issues where the circuit breaker is rated properly for the FLA of the motor, but you can't adjust the inrush high enough to get the motor to start. This has happened in several instances in the plant that I work at - we replace a grounded motor with a new high efficiency one, but then the breaker keeps tripping on start-up. Then you have to replace either the whole bucket or just the breaker itself, but with the latter you can get in trouble with having to adjust the bucket lever linkage, etc. Not fun.
I believe the limit imposed by the NEC is the breaker can be rated 250% of the motor FLA as a maximum.