430.21 states that motor conductors must have an ampacity of 125% of the motor full load current, as determined by the NEC tables. My supervisor and I have a disagreement about the required conductor size.
We are installing 75 Hp motors, 480V, 3 phase, the full load current from the table is 96 amps.
96A X 1.25 = 120A (required ampacity of the conductor)
Here's where we disagree. We are running #1 THHN, 6 current carrying conductors in a conduit (two motors). They need to be derated to 80%. The ambient temperature is also 46-50C, so they also need an additional derate to 82% of the ampacity calculated by the CCC derate.
#1 THHN = 145A X .80 X.82 = 95.12 ampacity (after applying the derating factors)
His calculations are as follows. 96FLA X 125% (this is the 80% derate for current carrying conductors) X 122% (this is the .82 derate for temperature)
So, 96 X 1.25 X 1.22 = 146.4 amps, it'll be fine since the nameplate current is less than the book, and we don't have to worry about the 125% conductor sizing required by 430.22 since the table value of a THHN conductor is 145 amps, well over the required 120 amps. The derates only are used to see if the conductor ampacity calculation is large enough to carry the load, which in this case is the motor FLA at 96A. Which as shown above, calculates to 95.12 amps.
How do you guys do your calculations?
We are installing 75 Hp motors, 480V, 3 phase, the full load current from the table is 96 amps.
96A X 1.25 = 120A (required ampacity of the conductor)
Here's where we disagree. We are running #1 THHN, 6 current carrying conductors in a conduit (two motors). They need to be derated to 80%. The ambient temperature is also 46-50C, so they also need an additional derate to 82% of the ampacity calculated by the CCC derate.
#1 THHN = 145A X .80 X.82 = 95.12 ampacity (after applying the derating factors)
His calculations are as follows. 96FLA X 125% (this is the 80% derate for current carrying conductors) X 122% (this is the .82 derate for temperature)
So, 96 X 1.25 X 1.22 = 146.4 amps, it'll be fine since the nameplate current is less than the book, and we don't have to worry about the 125% conductor sizing required by 430.22 since the table value of a THHN conductor is 145 amps, well over the required 120 amps. The derates only are used to see if the conductor ampacity calculation is large enough to carry the load, which in this case is the motor FLA at 96A. Which as shown above, calculates to 95.12 amps.
How do you guys do your calculations?