- Location
- Connecticut
- Occupation
- Engineer
Read what I said again, I was talking about a non continuous duty motor in what you quoted. I did not go much further than that but in general the motor will have a duty rating if this is the case.
I did read what you said, and it mentioned "continuous load" not continuous duty motor.
If the motor is not continuous load 430.22 doesn't apply
The only thing that will change my opinion of how I determined 1/0 was needed for the OP, is if you can convince me the 125% in 430.22 also applies to determining ampacity based on insulation temp.
430.22 says the motor circuit conductor shall have an ampacity not less than...in the OP's example that ampacity value is 120. In the OP example #1/0 THHN would have an ampacity of 112. 112 is less than 120. I don't think it could be any simpler than that.
I do realize there is nothing that says it is allowed to exclude that, but at same time if same current were on the conductor and it was anything but a motor, it could be 1/0, but could also never be smaller than 1 AWG when it comes to termination rating.
If there is nothing that says it is allowed to exclude that, why are you trying to exclude that. Yes, if the load was anything else but a motor then it could be 1/0. BUT, the rules for motors vs. other loads are different. You are still trying to apply 210.19 even though you agree that 210.19 doesn't apply. The motor circuit conductors must comply with Article 430, and your approach doesn't comply.