I have a couple of questions about tapping the motor circuit conductors at the motor for the installation of a power factor correction system. The equipment to be installed has a 50 amp OCPD and the motor is a 200 hp, 480 volt motor.
1) Are motor circuit conductors between the controller and the starter branch circuit conductors? If so, then 210.19 would apply and make the installation a code violation. I am assuming that 210.19 does not apply because the installation of power factor correction equipment at the motor is not uncommon.
2) Assuming that I can use the feeder tap rule in 240.21(B)(2) can I use the rating of the motor overload protector to size the tap conductors.
Don
1) Are motor circuit conductors between the controller and the starter branch circuit conductors? If so, then 210.19 would apply and make the installation a code violation. I am assuming that 210.19 does not apply because the installation of power factor correction equipment at the motor is not uncommon.
2) Assuming that I can use the feeder tap rule in 240.21(B)(2) can I use the rating of the motor overload protector to size the tap conductors.
Don