loosewire64
Member
I have a large chiller project that has 4 motor control centers. This is an add-on project and we have added an additional section to an existing MCC. This is done as a subsection rated at 500amps and fed from a 500amp existing breaker in the existing MCC. The new section was specified as 3phase 4wire and the existing sections which are SE rated are 3phase 3wire (2000amp MCB). In the existing MCC there is a distribution panel built in that has 5-1P/20amp breakers feeding the interior lighting. We have a new 100a 3phase panel being fed from the new section for additional interior and exterior lighting. The exisiting MCC has 6-500MCM conductors per phase and 6-250MCM conductors connected to the ground buss from the utility transformer. We have verified the 250's are connected to XO in the utility transformer. I have contacted the design engineer for the project and requested guidance on how he wishes to connect the neutral conductors. The existing distribution section is getting it's nuetral from the ground buss. The engineer is directing us to connect our 2-250MCM nuetrals to the ground buss to act as our nuetral for the new section. He also wants us to connect our 2-#2 equipment ground conductors to the same bar. My concern is we will then be connecting a labeled 4wire MCC to a labeled 3wire MCC and getting our neutral from the ground buss which is only 1" wide. I have told the engineer I believe by code we cannot connect to anything that is not properly labled for the connection. He say's since it is an industrial application it is allowed. Does anybody have opinion or fact based thought on this?