erickench
Senior Member
- Location
- Brooklyn, NY
NEC 250.30 state's that the system bonding jumper can be made at any single point on the separately derived system from the source to the first system disconnecting means. In this case the MCC would be the first system disconnecting means. Since there is no neutral terminal bar you can either field install it or just install the SBJ at the transformer and run your jumper.