I have a customer wanting a setup as follows....
He has a 7.5 3phase motor driving a grain auger. He would rlike the following to happen. When the motor driven auger is loaded (is actually moving grain), for a small 120v 3amp pump to kick on and treat grain w/ some kind of chemical. When the 7.5 horse motor is off, OR, if the 7.5 horse motor is not loaded, (running the auger, but no grain to move), the small electric pump shuts off. When the auger is again loaded, the pump restarts. My thoughts are that to shut the pump on/off, would be done by reading amps of 7.5 motor. Could i use a overload relay, set the overloads to trip when the motor pulls more amps than at empty auger, and run a contactor w/ coil controlled by auxillary contacts of overload relay? Clear as Mud? I think it will work but thought I would ask you guys...Thanks ahead..
He has a 7.5 3phase motor driving a grain auger. He would rlike the following to happen. When the motor driven auger is loaded (is actually moving grain), for a small 120v 3amp pump to kick on and treat grain w/ some kind of chemical. When the 7.5 horse motor is off, OR, if the 7.5 horse motor is not loaded, (running the auger, but no grain to move), the small electric pump shuts off. When the auger is again loaded, the pump restarts. My thoughts are that to shut the pump on/off, would be done by reading amps of 7.5 motor. Could i use a overload relay, set the overloads to trip when the motor pulls more amps than at empty auger, and run a contactor w/ coil controlled by auxillary contacts of overload relay? Clear as Mud? I think it will work but thought I would ask you guys...Thanks ahead..