It appears that the 2005 NEC Handbook Art 430.102(A) requires that the location of the disconnect for controllers be with insight.
The Exception allows the disconnect to be installed remotely if over 600v.
430.102(B) requires the disconnect for motors to be installed within site.
The Exception allows the motor disconnect means to be installed remotely providing they comply with (a) or (b) and providing they comply with 430.102(A).
Can it be said that disconnect means for motors and controllers only be mounted remotely if 600v and over and impracticable of being mounted in the location of being insight of the motor and equipment?
the commentary expresses this.
Zane.