I did design for a 50 HP Soft-Start on a submersible pump, sizing the controller and cable for 50HP, based on the motor amperages in 430.250 - Full-Load Current, Three Phase Alternating -Current Motors.
The motor draw has been measured to be 77 amps @ 460V, equating to 60 HP per NEC 430.250 - resulting in death of the soft-start.
The civil engineering firm that gave me the 50HP number says the town may be asking my company for reimbursement to upgrade the controller to 60 HP. I tell him that my design is adequate for 50 HP, as directed. And, if he was confident in his calculation of 50 HP, look for some other problem like pipe restriction on the outlet that may be causing high power requirement. Otherwise, he underestimated the pump motor requirement.
And the only thing that has me doubting the basis of the design is "Service-factor" of a motor. If the motor has a 1.2 SF, that would cause the controller to see 60 HP of load. I think this one has a 1.15, (I never saw the motor submittal to verify nameplate data), and I think the 50 HP Soft-Start may have handled that. But this measured load is at 118.5% of fla.
I always size everything for "minimum-essential", that being the smallest size that adequately meets the criteria. To me that's good-engineering not to over-design at the expense of a client. The tables are there to be "sized to".
In this case if I were made aware that the load was going to be 60 HP, I would have sized to that, and there wouldn't have been a problem.
Thanks for any commentary.
JM
The motor draw has been measured to be 77 amps @ 460V, equating to 60 HP per NEC 430.250 - resulting in death of the soft-start.
The civil engineering firm that gave me the 50HP number says the town may be asking my company for reimbursement to upgrade the controller to 60 HP. I tell him that my design is adequate for 50 HP, as directed. And, if he was confident in his calculation of 50 HP, look for some other problem like pipe restriction on the outlet that may be causing high power requirement. Otherwise, he underestimated the pump motor requirement.
And the only thing that has me doubting the basis of the design is "Service-factor" of a motor. If the motor has a 1.2 SF, that would cause the controller to see 60 HP of load. I think this one has a 1.15, (I never saw the motor submittal to verify nameplate data), and I think the 50 HP Soft-Start may have handled that. But this measured load is at 118.5% of fla.
I always size everything for "minimum-essential", that being the smallest size that adequately meets the criteria. To me that's good-engineering not to over-design at the expense of a client. The tables are there to be "sized to".
In this case if I were made aware that the load was going to be 60 HP, I would have sized to that, and there wouldn't have been a problem.
Thanks for any commentary.
JM