I have an energy management company installing fan relays on exhaust fans in schools. They are using RIB relays and class 2 wiring back to a network based controller to shut off exhaust fans after hours to conserve energy. They are mixing class 2 wiring and electric light and power in the same raceways and enclosures, and claiming they are exempt from NEC rules because the state exempts temperature control contractors from licensing and inspections. They are installing 1/2 HP rated relays on 120 V circuits, which have multiple motors/exhaust fans. They are not checking the HP ratings on the motors on the circuit. I have told them that the HP rating is for individual motors based on the locked rotor current. They are trying to claim that the relays are rated for 20 amps, and as long as its "not tripping the breaker" they are ok with what they are doing.They are also using double pole RIB relays and putting two separate circuits derived from two separate panelboards and two separate OCD to control two separate motors.Obviously they don't have a clue what they are doing. Anyone else have a problem with these types of "energy management contractors"? We are talking a big company here that is nationwide and their Project Manager claimed to me that nobody has ever taken them to task before. I'm just a concerned electrical QC person working in a big (60+ schools) school district. When somebody boasts they are doing this type of work all over my state and the US and nobody has ever complained in his "15 years with the company", it really makes me wonder.