Motor disconenct required?

Status
Not open for further replies.
Is a motor operated 1" fuel valve required to a have a local disconnect as required 430.102?
It seems that for such a small motor, that this requirement is silly.

Its required, but does not have to be anything elaborate, or even something that has to be added.

Take a look at 430.109 (B) and (C).
 
What size motor. 430.109 (B) says no disco required if the stationary motor is less than 1/8th Hp. If it's less than 1/8th hp, then no disco is required. The OCPD is the disco in this scenario.
 
What size motor. 430.109 (B) says no disco required if the stationary motor is less than 1/8th Hp. If it's less than 1/8th hp, then no disco is required. The OCPD is the disco in this scenario.
More precisely, does it not say the branch circuit overcurrent device shall be permitted ?
I never thought of it, but does this remove the requirement of 430.102 (B)(1) ?
 
Status
Not open for further replies.
Top