Is a disconnecting means not required within site of a hardwired motor if the motor is 1/8 hp or less (and motor is not an appliance)?
As per 430.109(B), the branch circuit overcurrent device can serve as the disconnecting means, but does OCD have to be within site as required by 430.102(B)? I know a lot of people interpret 430.109(B) to mean a switch at the motor isn't required, but where in code is this allowed? (But at the same time, if a switch is required at the motor, this seem inconsistant with appliance section 422.32 that only requires disconnect within site if motor > 1/8 hp.)
Also what does protecting a person from getting zapped by a 20 amp branch circuit have to do with whether it is connected to a 1/7 Hp or 1/8 hp load?
As per 430.109(B), the branch circuit overcurrent device can serve as the disconnecting means, but does OCD have to be within site as required by 430.102(B)? I know a lot of people interpret 430.109(B) to mean a switch at the motor isn't required, but where in code is this allowed? (But at the same time, if a switch is required at the motor, this seem inconsistant with appliance section 422.32 that only requires disconnect within site if motor > 1/8 hp.)
Also what does protecting a person from getting zapped by a 20 amp branch circuit have to do with whether it is connected to a 1/7 Hp or 1/8 hp load?