Motor Disconnect Switch

The general rule is 115% of the motor FLA other than no-fuse switches. As infinity notes most switches are HP rated. A quick look at most manufacturer catalogs will show you amperage & HP
 
Has anyone ever seen a disconnect switch with a HP rating that was actually less than the 115% that Augie mentioned?
 
Has anyone ever seen a disconnect switch with a HP rating that was actually less than the 115% that Augie mentioned?
No, I have never seen that.

Which begs the question as to why the NEC allows it in the exception to 430.110(A)! I imagine that at one point in the past, someone must have made a "HP rated switch" that did not meet the 115% rule, i.e. it was rated somewhere between 100% and 115% of the specific motor FLC. Most likely some dedicated OEM part where the manufacturer was shaving pennies on high volume production.

Side note: that 115% rule does NOT apply below 2HP (430.109(C)). If you want to use a "general purpose" snap switch that does not have a specific HP rating. In that case, the switch must be 2x the motor FLA, or if identified as "only for use on AC", it is 125% (inverse of 80% rule).
 
Has anyone ever seen a disconnect switch with a HP rating that was actually less than the 115% that Augie mentioned?
Isn't there a top end for HP switches? I haven't looked but in my mind bolted pressure switches didn't have HP ratings nor did MV switches.
 
Which begs the question as to why the NEC allows it in the exception to 430.110(A)! I imagine that at one point in the past, someone must have made a "HP rated switch" that did not meet the 115% rule, i.e. it was rated somewhere between 100% and 115% of the specific motor FLC.
I asked because I seem to remember a scenario in the field years ago where the HP rating of the switch was less than the 115%. If I had to guess the numbers were very close as far as being just under the 115%.
 