What is the size of a motor disconnect switch based off of? How would one calculate? Is it the breaker size feeding it?
Not necessarily. As mentioned 115% is the general rule. Inverse time breakers can be 250% of FLA to allow motor starting.Is it the breaker size feeding it
No, I have never seen that.Has anyone ever seen a disconnect switch with a HP rating that was actually less than the 115% that Augie mentioned?
Isn't there a top end for HP switches? I haven't looked but in my mind bolted pressure switches didn't have HP ratings nor did MV switches.Has anyone ever seen a disconnect switch with a HP rating that was actually less than the 115% that Augie mentioned?
I am used to looking at the voltage and HP rating of the disconnect . 430.110 gives more info.What is the size of a motor disconnect switch based off of? How would one calculate? Is it the breaker size feeding it?
I asked because I seem to remember a scenario in the field years ago where the HP rating of the switch was less than the 115%. If I had to guess the numbers were very close as far as being just under the 115%.Which begs the question as to why the NEC allows it in the exception to 430.110(A)! I imagine that at one point in the past, someone must have made a "HP rated switch" that did not meet the 115% rule, i.e. it was rated somewhere between 100% and 115% of the specific motor FLC.
Yes, I remember a similar situation. IIRC, it was a 30 Amp disconnect. I had to move up to a 60. IDR if it was 1 or 3 phase.I asked because I seem to remember a scenario in the field years ago where the HP rating of the switch was less than the 115%. If I had to guess the numbers were very close as far as being just under the 115%.