would a manual starter with a lock out device on the stop button be considered a motor disconnect located within sight of the motor?
How would this be possible if the disconnecting means was a CB?I seem to recall some kind of requirement that you be able to visually inspect the poles of a disconnecting device for proper function
Note that there is no requirement that it be lockable at all, simply marked "suitable." In fact, Section 403.102 does not require any disconnect, motor or controller, to be lockable as long as at lease one of them is ?in sight? from the motor. The product standards (NEMA & UL)for most acceptable disconnecting means do have a provision for locking but it is not a direct NEC requirement.430.109(A)(6) Manual Motor Controller. Listed manual motor controllers additionally marked ?Suitable as Motor Disconnect? shall be permitted as a disconnecting means where installed between the final motor branch-circuit short-circuit and ground-fault protective device and the motor.