I am currently in a discussion with an inspector about the need for disconnects immediately adjacent to sewage aeration ponds, to disconnect floating aerators located out in the open ponds. The power for each aerator and blower come from a motor control center located between 100? and 600? away from the blowers depending on which one is being measured. The blowers are all 480 volt 3 phase, and vary from 2 hp to 20 hp.
I based my design on NEC 430.102(B)(2) Exception a and b. The sewer plant is fenced and locked, and you either need a boat to get to these blowers, or you need special training to pull them into shore.
The inspector is insistent that there be a disconnect, in fact he is now asking for cord caps and receptacles at the shore connection.
Does anyone have an opinion about my contention, or the inspectors? Should there be a second disconnect at the pond even though the disconnect at the MCC disconnects the controller and is lockable?
Thanks in advance for any thoughts.
Jim T
I based my design on NEC 430.102(B)(2) Exception a and b. The sewer plant is fenced and locked, and you either need a boat to get to these blowers, or you need special training to pull them into shore.
The inspector is insistent that there be a disconnect, in fact he is now asking for cord caps and receptacles at the shore connection.
Does anyone have an opinion about my contention, or the inspectors? Should there be a second disconnect at the pond even though the disconnect at the MCC disconnects the controller and is lockable?
Thanks in advance for any thoughts.