I have a 460v 3 phase 60 hp motor. I have a #4 starter and #3 wire for hookup. I need to know what size breaker to use. All the info I have found indicates a 200 amp breaker. Is this correct?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Ahhhh for the good old days of suppliers giving out free “slide charts” for motor starters. They told you everything you needed to know; starter sizes, breakers, fuses, conductor sizes, heater element selection etc. You youngsters have to struggle now to find that info or buy an old slide chart on ePay or Amazonk.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Ahhhh for the good old days of suppliers giving out free “slide charts” for motor starters. They told you everything you needed to know; starter sizes, breakers, fuses, conductor sizes, heater element selection etc. You youngsters have to struggle now to find that info or buy an old slide chart on ePay or Amazonk.
I may have part of my retirement laying around in various file drawers.
 

tom baker

First Chief Moderator
Staff member
Ahhhh for the good old days of suppliers giving out free “slide charts” for motor starters. They told you everything you needed to know; starter sizes, breakers, fuses, conductor sizes, heater element selection etc. You youngsters have to struggle now to find that info or buy an old slide chart on ePay or Amazonk.
When I instructed classes on Art 430 I bought the slide rule charts in bulk from American slide rule company. On eBay they are $$. I had many from different code cycles, what’s nice is the Art 430 tables have not changed
 
Last edited:

Johnh3375

Member
Location
Lenexa kansas
Occupation
Maintenance manager
All the electricians I have had bid on this job wanted to use a 80 amp breaker. One even refused to do the job because I didn't agree with him and sent him the appropriate section of code 430.52
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
This one’s a 1990 vintage. Made sure I got it out of the truck before I turned it in last week!
 