We have a site where they are installing a new chiller, cooling tower and associated pumps and we are questioning the size of the distribution board and feeder conductors feeding this equipment. I believe I've attached a partial single line diagram.
Loads
(1) 800 Ton Chiller (Primary RLA = 548A, MCA = 694A)
(1) 30 HP Cooling Tower Fan (FLA = 40A)
(1) 50 HP Condensor Water Pump (FLA = 65A)
(1) 100 HP Chilled Water Pump (FLA = 124A)
Per 430.24 ampacity of conductors = 125% of Largest motor + sum of FLA of other motors.
Using Chiller RLA as largest motor I come up with 548A x 125% = 685A + 40A + 65A + 124A for a total of 914A required for motor feeder conductor size.
Based on that calculation, can these loads be fed from an 800A 100% rated circuit breaker that is feeding an 800A 100% Rated distribution board?
215.3 allows for sum of continuous + non-continuous loads for 100% rated breakers, but how do motors transpose in that? Example D3(a) in Annex D uses the 125% of largest motor + sum of other motors to determine ampacity of motor loads and then adds that to the non-continuous loads for the total feeder calculation.
Scratching my head on this one.
Loads