I am an apprentice hoping to gain an understanding of motor calculations, the question I am working on is this.
"What is the minimum size inverse time breaker needed to protect a feeder with "TW" insulation supplying two 1hp single-phase 115V motors?"
This is what I have come up with so far:
1. FLC = 16A (Table 430.148)
2. Overload heater sized at:
16A x 1.15% = 18.4A rated heater 430.32 (B,1)
3. Branch circuit wire size:
16A x 1.25 = 20A # 14 TW Table 316.10
4. Branch circuit OCP:
16A x 2.50 = 40A ocp 430.52, Table 430.52
5. Feeder wire size:
16A x 1.25 = 20A + 16A = 36A # 8 TW 430.24, Table 310.16
This is where I lose my train of thought. Is this method correct?
6. Feeder OCP (using inverse time breakers):
16A x 2.50 = 40A + 16A = 56A but this is a motor feeder so I need to down size to a 50A ocp??? 430.62, 240.4 (G)
Is the math in step six the correct method? Any help would be great.
Thank,
Kevin
"What is the minimum size inverse time breaker needed to protect a feeder with "TW" insulation supplying two 1hp single-phase 115V motors?"
This is what I have come up with so far:
1. FLC = 16A (Table 430.148)
2. Overload heater sized at:
16A x 1.15% = 18.4A rated heater 430.32 (B,1)
3. Branch circuit wire size:
16A x 1.25 = 20A # 14 TW Table 316.10
4. Branch circuit OCP:
16A x 2.50 = 40A ocp 430.52, Table 430.52
5. Feeder wire size:
16A x 1.25 = 20A + 16A = 36A # 8 TW 430.24, Table 310.16
This is where I lose my train of thought. Is this method correct?
6. Feeder OCP (using inverse time breakers):
16A x 2.50 = 40A + 16A = 56A but this is a motor feeder so I need to down size to a 50A ocp??? 430.62, 240.4 (G)
Is the math in step six the correct method? Any help would be great.
Thank,
Kevin