I looked at a job today where I am going to wire two 75HP compressors. I'd like to have some eyeballs go over my plan. Here's what I have:
Switchboard with existing Westinghouse 400 amp CB (where the trip unit can be changed out to reach up to 800 amps). It is an LM frame style. I hope to leave the CB alone but I suspect I need to change the trip unit.
The compressors will be fed through a new transfer switch so only one can run at a time. The load side(s) of the transfer will feed two fused disconnects. One for each compressor package.
Compressor packages come with internal starters and other controls. One of the packages comes with a built-in VFD for soft starting, etc. and the instructions say to just supply it through fused disconnect with class J fuses. The max starting amps of the unit is 221. The chart on the instructions say to provide a max fuse of 300 amps for this unit.
The non-VFD compressor package has a standard hard start starter and the FLA is 228 amps. The instructions say to use a time delay fuse. So I multiply by 175% to arrive at 400 amp fuse size.
To determine feeder wire size to the transfer switch I multiplied 228 FLA times 125% (= 285 amps) so I figure I will use 300 MCM copper THHN.
To determine feeder breaker size I figured 228 amps times 250% to arrive at 570 amps. So I figure the 400 amp existing breaker is too small.
Any comments? How much did I get wrong? Any responses would be appreciated.
Switchboard with existing Westinghouse 400 amp CB (where the trip unit can be changed out to reach up to 800 amps). It is an LM frame style. I hope to leave the CB alone but I suspect I need to change the trip unit.
The compressors will be fed through a new transfer switch so only one can run at a time. The load side(s) of the transfer will feed two fused disconnects. One for each compressor package.
Compressor packages come with internal starters and other controls. One of the packages comes with a built-in VFD for soft starting, etc. and the instructions say to just supply it through fused disconnect with class J fuses. The max starting amps of the unit is 221. The chart on the instructions say to provide a max fuse of 300 amps for this unit.
The non-VFD compressor package has a standard hard start starter and the FLA is 228 amps. The instructions say to use a time delay fuse. So I multiply by 175% to arrive at 400 amp fuse size.
To determine feeder wire size to the transfer switch I multiplied 228 FLA times 125% (= 285 amps) so I figure I will use 300 MCM copper THHN.
To determine feeder breaker size I figured 228 amps times 250% to arrive at 570 amps. So I figure the 400 amp existing breaker is too small.
Any comments? How much did I get wrong? Any responses would be appreciated.