erickench
- Brooklyn, NY
Don, I would like to point your attention to NEC 675.7(A). It states:
The equivalent continuous-current rating for the selection of branch-circuit conductors and overcurrent protection shall be equal to 125 percent of the motor nameplate full-load current rating of the largest motor, plus a quantity equal to the sum of each of the motor nameplate full-load current ratings of all remaining motors on the circuit multiplied by the maximum percent duty cycle at which they can continuously operate.
As you can see the motors for an irrigation machine are fed from a circuit that pretty much resembles a feeder in that there is more than one motor included in the machine. There is no reference to NEC 430.52 although Stallcups references it in his book "Electrical Calculations Simplified" and performs the calculation in accordance with NEC 430.52 and NEC 675.7(A).
NEC 675.7(A) performs the calculation in a similar matter to NEC 430.24. It's pretty clear that this NEC rule is requiring an overload but no short-circuit ground-fault protection.