NEC newb here. I'm a litte confused with article 430.62
It says that the rating of a motor feeder protective device is determined by adding the rating of the largest branch-circuit protective device for any motor supplied by the feeder to the sum of the full-load currents of all of the other motors supplied by that feeder.
What I have: 480VAC into a panel with two 25HP soft starts. According to my calculation, each motor has a FLC of 34 amps and should be fused for 51 amps. I'm trying to size the feeder circuit breaker. Do I need an 85 amp breaker or do I use the sum of 85 to size the breaker?
Thanks!