I am not a huge fan of fuses for various reasons.
One reason is the need to have a set of spare fuses on hand for every size and type of fuse in the plant so that when one blows, you can replace it. Often it seems like the rating you need is not available so you end up putting in whatever you can find that fits in the fuse block just to get back and operating, always with the intent of getting the correct rating, but it does not always happen.
As an integrator, another reason I don't like fuses is because over about 100A they usually cost more then a MCCB and take up more space. They also have more options for being able to be locked out that is less available with fuses. MCCB also have more/better options for lugs in many cases than fuse blocks do.
However, if you need a high SCCR, fuses are often a cost effective answer.
I find myself using fuses mostly 60A and smaller. That seems to be the break point for me where fuses become less practical and a MCCB starts to make more sense. I have gravitated toward class CC fuses for 30A and under and class J fuses for 60A sizes. One reason I like the class CC fuse blocks because you can now get 1,2, and 3 phase bus bars for them. Makes wiring a lot simpler.
Siemens and AB both have UL489 mini breakers now that have bus bar options, but they are only good for 10kAIC, so that limits their usability, even though they are rated for up to 480/277V. Even so they are pretty cost effective and take up very little space. Pretty good for small motors.
thank you for your input, I didn't see your post till now.
I agree fuses are pricy,
migets are what 10 bucks a piece or more?
and if you have two troublshooting calls you can blow 4-6 easy, if you are in a hurry and don't check stuff.
thats 60 bucks out the window!
and thats a fuse less than 35 amps!
Breakers are good because they open all phases, and reduce the possibility of single phasing.
but one thing I have seen and sort of have a question about is current limiting ability.
I have ohmed out fuses on a Reliance VFD drive before and they were closed, and not open.
but when turned on, there was some voltage but not all voltage on second half of fuse.
is this part of the current limiting aspect of a fuse, or is it simply a partially blown fuse, (maybe one of the dual elements gone)?
but I guess what I don't get is why the voltage there was voltage drop.
yeah, it must be the current limiting ability create more and more resistance, and slowly creates greater voltage drop, till it's gone.
( I guess I answered that myself)
but some guys I train don't believe me that you need to check voltage on both sides of fuse, sometimes they are bad, but ohm good.
which means you need to do it live.
against company policy, sometimes.
with the current NFPA 70E you have to pretty much be an astronaut to do what I mentioned above.
But I believe if you are troubleshooting 110 there is an exception that is similiar to the now non existent category zero.
but I dont' remember, since it's been 6 months.
which reminds me, if you see any long tail FR clothing, on sale, let me know.
I have been buying long tees from a tee shirt online, but if I can fine a FR rated one, it will add Calories to my existing over shirt/pants.
and if I have to remove the over coat for some reason, at least I will have still a FR shirt below.
instead of cotton right now.