The numbers I gave earlier are for 3 seperate compressors. They are not 3 different input amps for the same compressor. Sorry if that caused confusion. I have some equipment that will use a cascade refrigeration system, so it will have 2 compressors. The system 2 compressor wil draw way more amps, at times, than the system 1 compressor. What is the proper way to represent the amps and HP on this equipment?
Seems like i would be better off finding the max operating current for system one, the corresponding KW, and then converting that to HP and using the tables in 430. Then, do the same thing for the other system.
The compressors do not come with an RLA on the nameplate, there is an RLA published by the manufacturer along with the Max operating current. There are actually two different RLA's, one for sizing conducters and overcurrent protection, and one for sizing contactors. The Max operating current is where the internal overload is set.
What is the correct way to size the mains and mains overcurrent protection? Using NEC 440, i am directed to the nameplate RLA. There is not a nameplate RLA, but there is one published. The equipments Running Load Amps can exceed this Rated Load, and also fall below the running load.
I have found that using the manufacturers publish RLA, and then using the FLA for other heaters and motors in the equipment is , spot on the FLA of the equipment. In fact, this method has never produced an FLA below the measured worst case FLA. I am just not sure that using the RLA of a compressor to get a HP, and then using that HP to size the feeder circuit breaker is correct. Would i need to take the max current the compressor draws and then convert that to HP and then use that as my largest motor HP?
Seems like i would be better off finding the max operating current for system one, the corresponding KW, and then converting that to HP and using the tables in 430. Then, do the same thing for the other system.
The compressors do not come with an RLA on the nameplate, there is an RLA published by the manufacturer along with the Max operating current. There are actually two different RLA's, one for sizing conducters and overcurrent protection, and one for sizing contactors. The Max operating current is where the internal overload is set.
What is the correct way to size the mains and mains overcurrent protection? Using NEC 440, i am directed to the nameplate RLA. There is not a nameplate RLA, but there is one published. The equipments Running Load Amps can exceed this Rated Load, and also fall below the running load.
I have found that using the manufacturers publish RLA, and then using the FLA for other heaters and motors in the equipment is , spot on the FLA of the equipment. In fact, this method has never produced an FLA below the measured worst case FLA. I am just not sure that using the RLA of a compressor to get a HP, and then using that HP to size the feeder circuit breaker is correct. Would i need to take the max current the compressor draws and then convert that to HP and then use that as my largest motor HP?