Background:
40hp, 4pole, Design B, Code G, 47.7FLA, meets MG-1 standards for "energy efficiency", factory test data shows LRA at 287A - which is consistent with a Code G (both NEC and MG-1).
Motor will occasionally trip (on startup) the instantaneous CB when set to 600A. Does not trip when CB set to 800A. There does not appear to be any thing wrong with the motor. Megger is fine, phase voltages are pretty even (within in a few percent), running current is about 60% FLA and also within a few percent.
The Question:
If the motor is spinning backwards when started, will (can) this increase the inrush current?
I can see a failure mode where this could happen. But, I can't get at the motor right now to see if this is happening - hopefully I'll be able to get at it later.
And I don't have any reference books here to go through a motor model to see how I might expect it to behave - next week I will.
Another interesting piece: I called the mfg engineering and asked about reverse rotation on starting affecting the inrush current. Response was, "This is outside of the operating envelope. We have no data on that scenerio."
Any insight will be graciously appreciated.
cf
edited to fix the factory LRA and FLA
40hp, 4pole, Design B, Code G, 47.7FLA, meets MG-1 standards for "energy efficiency", factory test data shows LRA at 287A - which is consistent with a Code G (both NEC and MG-1).
Motor will occasionally trip (on startup) the instantaneous CB when set to 600A. Does not trip when CB set to 800A. There does not appear to be any thing wrong with the motor. Megger is fine, phase voltages are pretty even (within in a few percent), running current is about 60% FLA and also within a few percent.
The Question:
If the motor is spinning backwards when started, will (can) this increase the inrush current?
I can see a failure mode where this could happen. But, I can't get at the motor right now to see if this is happening - hopefully I'll be able to get at it later.
And I don't have any reference books here to go through a motor model to see how I might expect it to behave - next week I will.
Another interesting piece: I called the mfg engineering and asked about reverse rotation on starting affecting the inrush current. Response was, "This is outside of the operating envelope. We have no data on that scenerio."
Any insight will be graciously appreciated.
cf
edited to fix the factory LRA and FLA