About a dozen I built them out like a 13kv stress cone. 3m splicing tape i believe is rated to 69kv. Do not take a 4kv cable lightly it can be very dangerous. I used to work in a large federal research laboratory where they did cutting edge of science work. While I was there I recieved a bulletin about an electrician working for a federal lab. He aparently was troubleshooting a 2400v motor starter the only tester he had with him was a fluke 77 multimeter which was rated only to 1kv. The electrician presumed that the meter would read over range when he applied the leads. what happened in fact was the entire tester including the leads vaporized in his hands. The ionized air created a phase to phase short which lead to an arc blast which killed himkkaragory said:The theory behind the high voltage splice...
----------------------------
The procedure that you allude to seems to be more in line for 12 kV and above; have you made many 4 kV connections the way that you described?