Re: Motor Load on Transormer
No, he is being truthful. A transformer can, for very short periods of time, carry 300%. We do not change out our transformers that feed residential loads until they are loaded to 170%. Having 200% is not unusual but we don't like to see it.
It depends on the load profile for the installation. In the case I mentioned about residential loads, the load peaks around dinner time and people have dinner at different times, dish washers are going along with water heaters, etc. Other than that, there is not much load on a transformer. By the time it gets warm, the load goes away.
This same line of reasoning applies to your pump. the heavy load is at the startup. After the motor starts, you are now dealing with only the running amperes (nameplate, the from the tables). It doesn't hurt the transformer to see that kind of load.
You mentioned the 5 kVA transformer, that is not the load that the electric utility will see. the electric utility's transformer will see the load that is running and being fed from that transformer if it is on at the time.
The interesting thing is that I have never seen a 45 kVA pad mounted or pole mounted transformer. To the best knowledge I have, a 45 kVA is only built as a dry type and most electric utilities do not use dry types.
Tom, is this a dry type, pole mount, or pad mount transformer and are you sure of the size? The reason for the question is that dry types are much more sensitive to overloads that the mineral oil filled types (it takes oil a while to heat up).