The motor should be protected from burning up by a properly sized overload, not by a branch circuit breaker.Because I've replaced a lot of burned up motors.
The motor should be protected from burning up by a properly sized overload, not by a branch circuit breaker.Because I've replaced a lot of burned up motors.
That's not the breaker's fault.Because I've replaced a lot of burned up motors.
In my humble opinion it isn't smart to protect a 1HP motor with a 20A breaker. 15 is better than 20 but still a little large.
Why do you think that?
Because I've replaced a lot of burned up motors.
The motor should be protected from burning up by a properly sized overload, not by a branch circuit breaker.
Perhaps not, but let's get back on track here and take that a few degrees of exaggeration higher to see what y'all have to say: same motor and properly overload protected on a 100A breaker?That's not the breaker's fault.
The motor should be protected from burning up by a properly sized overload, not by a branch circuit breaker.
The motor should be protected from burning up by a properly sized overload, not by a branch circuit breaker.
He also failed to provide further information when asked for it, well sort of. Did turn the topic of discussion towards general purpose receptacle outlets to some extent, yet the example he gave but did not confirm was his application in OP was for a 1 hp 480 volt three phase motor. If it were a 120 volt 1 hp single phase motor we maybe are agreeing that 20 amp breaker is fine, maybe even necessary. Reality is 15 amps is overkill for a 1 HP 480 volt three phase motor, yet would be allowed by code.True but the OP didn't mention any overload, only the breaker.
Perhaps not, but let's get back on track here and take that a few degrees of exaggeration higher to see what y'all have to say: same motor and properly overload protected on a 100A breaker?
but that would not leave us with 100 amp setting for the motor short circuit and ground fault protection if it were installed on a 100 amp feeder, it essentially becomes the branch circuit protective device, with overload protection set per the dial and a magnetic trip setting that is fixed - but is probably much less then 100 amps if the device is properly selected for said 1 HP 480 volt three phase motor.No problem with that. I like these Allen Bradley 140M Motor protective circuit breakers. They have both thermal and magnetic trips.
woudn't 430.52 still require a maximum setting of 250% of motor FLA for inverse time breaker or 800% for instantaneous time breaker? Only if those values won't let the motor start are you permitted to go higher? If OP's motor is 1 hp 480V 3 phase, 100 amps is well above those figures.Perhaps not, but let's get back on track here and take that a few degrees of exaggeration higher to see what y'all have to say: same motor and properly overload protected on a 100A breaker?
Yes. And I was attempting to get other participants back on this track.woudn't 430.52 still require a maximum setting of 250% of motor FLA for inverse time breaker or 800% for instantaneous time breaker? Only if those values won't let the motor start are you permitted to go higher? If OP's motor is 1 hp 480V 3 phase, 100 amps is well above those figures.
Yes. And I was attempting to get other participants back on this track.
It simply comes down to, the NEC permits a 15A [typical thermal-magnetic panelboard] breaker only because it is the smallest standard breaker rating. Only on the very rare occasion where the motor of topic trips the breaker on start up would one be permitted to go to a 20A breaker.
but that would not leave us with 100 amp setting for the motor short circuit and ground fault protection if it were installed on a 100 amp feeder, it essentially becomes the branch circuit protective device, with overload protection set per the dial and a magnetic trip setting that is fixed - but is probably much less then 100 amps if the device is properly selected for said 1 HP 480 volt three phase motor.
I don't know about lawyers, but you hopefully learn when inspectors catch what may seem like minor details and you then have a mindset to look for such details.I agree you shouldn't have a 100 amp circuit feeding a 1HP motor with only an overload. I need to read more closely before posting. You guys should have been lawyers.
Let's just say clever...Were you really setting us up or was that a clever bail out?
Perhaps not, but let's get back on track here and take that a few degrees of exaggeration higher to see what y'all have to say: same motor and properly overload protected on a 100A breaker?