I understand machines and reactive power/elements (I think lol)
but this is a machine wound for 1 HP AT 230 operating on 208
1 HP FLA from tables
230 4.2 A
208 4.6
but we are running a 230 rated/wound for 1HP on 208
v = i (R + j X) in which the cos(arctan X/R) is the pf
ignoring R which is basically a property of the windings and is constant
in this case X is primarily inductive = 2 Pi f L
all constants except L which can be consider constant/linear since poles/winding/etc remains the same and v delta is small with the only impact being the current delta
230 = 4.2 X or X = 54.76 ohm
208/54.76 = 3.9 A
to go to 4.6 A which is the rating for 1HP 208
208/4.6 = 45.2 a decrease of 17% of L despite more current
???
http://www.baldor.com/catalog/CNM20134#mobile-tab={"component":"tab","tab":"performance"}
small motor
current and torque drops proportional to v
230 0.86 fla
208 0.78 fla
0.78/0.86 = 0.907
208/230 = 0.904
torque, pull up
230 432 lb-in
208 344 lb-in
344/432 = 0.8 (sq of v ratio) since power~ torque ~ sq of V
should hold for a larger motor??
hmmmmm